Is it ok to supply 120/208volt Y electrical service to a RV site in stead of 120/240?
I believe that the 50A are 240, but as I understand it, nothing in any commercial RV uses 240. It is common for one of the air conditioners (maybe more) to use 1 phase, the other AC and everything else to use the other.I just got done designing one, and I don't see a problem with it because the RVs don't use 240 or 208 power, they use a 30A receptacle @ 120V, and some use a 50A @ 120v.
Is it ok to supply 120/208volt Y electrical service to a RV site in stead of 120/240?
I had the option of using a 3 phase open delta service for my RV park but I realized I wouldn't be able to use the B phase for anything! (no 3 phase loads) So I went with the residential service type 240-1, better then 208-1 as far as service size is concerned.
If your doing an RV park, make sure you take voltage drop into account, they can be very lengthy. Good Luck