Air Conditioner O/C protection

Status
Not open for further replies.

rwreuter

Senior Member
here is something that has puzzled for me for some time. air conditioner unit overcurrent protection.

when i wired houses it was oh so common to see a name plate rating of a unit and then we would put a cb on it that was higher. why and was it correct.

i am now about to place a disco on my unit and the name plate states 40amps, but as it sits now i have it fed with a 6-3 w/ground copper and the breaker is a 60amp.

believe it or not, i am not sure if what i (we) did was right, just dumb ignorance on my part, doing what we were taught without knowing the how or why.

is a 60amp breaker good, bad or ugly and/or should i just place a 40amp in there and it will work fine. i am sort of assuming the name plate is taking into consideration the motor start up.

advice or a place to look would be great here.


rw
 

480sparky

Senior Member
Location
Iowegia
What number are you 'exceeding'? The 'Maximum Overcurrent Rating'? If so, you're creating a violation. If the nameplate states a MOR of 40 amps, installing a 60 should result in a red tag.

Replacing it with a 40 is only part of the potential problem. Another thing to check is the wire size.
 

rwreuter

Senior Member
wire size should not be an issue, i can go over but not under.

i just remember reading somewhere that air conditioners have "funny" rules that apply to them and their over current protection devices and odly enough their wire size.

just can't remember where i read it and whether or not it was a valid article or statement.



rw
 

rwreuter

Senior Member
for example....i just went over 440.22 (a)

"a protective device having a rating or setting not exceeding 175 percent of the motor compressor rated-load current or branc-circuit selection current, whichever is greater, shall be permitted provided.........."


if i understand this right (not sure if i do) then if the max ocpd is 40 and i multiply 40 * 175%, i get 70....so by this reasoning the 60amp ocpd is good.


make good or bad sense, or am i completely off of my rocker?



rw
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
when i wired houses it was oh so common to see a name plate rating of a unit and then we would put a cb on it that was higher. why and was it correct.

This is correct because a/c units usually need a higher amp. breaker to help it with the startup. The a/c unit has overload protection built in so the wire is protected from overload. The higher breaker will have no problems clearing a ground fault or short circuit.
 

480sparky

Senior Member
Location
Iowegia
wire size should not be an issue, i can go over but not under.

i just remember reading somewhere that air conditioners have "funny" rules that apply to them and their over current protection devices and odly enough their wire size.

just can't remember where i read it and whether or not it was a valid article or statement.



rw

The 'funny' rule is 240.4(G).
 

rwreuter

Senior Member
ok, lets look at 440.22 (c)

how do you all interpret that, comparing it to 440.22 (a)....

seems to contridict, or am i reading it incorrectly?



rw
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
ok, lets look at 440.22 (c)
how do you all interpret that, comparing it to 440.22 (a)....
seems to contridict, or am i reading it incorrectly?

I don't see it as a contradiction but rather as a trump of 440.22(A) &(B). Basically it limits you to what the manufacturers has marked on the unit for the maximum overload setting.
 

rwreuter

Senior Member
ok, now i am back to where i started

name plate: 40amp with a 60amp ocpd

just curious what is 440.22 (a) for then if the other paragraph trumps it? just an obviouse common sense question is all. oh wait, i can't ask that, dumb me....:(



rw
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
ok, now i am back to where i started

name plate: 40amp with a 60amp ocpd

just curious what is 440.22 (a) for then if the other paragraph trumps it? just an obviouse common sense question is all. oh wait, i can't ask that, dumb me....:(
rw
It probably doesn't trump it very often. I have never seen an a/c unit whose max OCP was less than 175%. I guess they exist for some specialized equipment.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
We went over this today already in the morning. http://forums.mikeholt.com/showthread.php?t=126009

I'm still confused/unsure about feeder vs branch circuit.

What does feeder vs branch circuit have to do with this discussion.:-?

Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).

Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
This is very simple. Look on the unit and it says min. circuit amps and max. breaker size. You can not go over the breaker limit. That is why they stamped that number. Now to select the wire size look at the min circuit amps. It never hurts to over size the wire and just might help in future when the unit is replaced and often for a larger unit or heat pump. The numbers are there so use them. Here the inspector will be checking and if your over you deserve a prize ,a nice red tag
 

hurk27

Senior Member
some older units will only have the FLA, and maybe the LRA, when this occurs I just apply 125% to the FLA for my circuit conductors and then apply the 175% for the breaker, this is of course if the label also stated the compressor has overload protection.

With newer units the 125% and 175% is built into the max and min. figure
 