Ok I have a unique situation I think I know the answer to but want a sanity check.
I am bidding out a 15 Kw grid tied system, but what makes it unique is the panels are 500 feet from the building mounted on a pole with 2-axis tracking. The system will consist of 7 strings. In the RFQ I quoted the feeder from the panels to the building be a 250 MCM to keep the power losses under 4%.
OK I get one bid back from a contractor that quotes running 15 #6 AWG or one pair of 6 AWG from each string plus 1 ground. I quized him about why and he replies the labor and cable will be less expensive. OK I don't have a problem saving money, but I am not sure running 7 feeders will comply with 690. I cannot find anything that prohibits it, nor do I find anything that allows it either. I just have never seen done this way.
What do you think.
I am bidding out a 15 Kw grid tied system, but what makes it unique is the panels are 500 feet from the building mounted on a pole with 2-axis tracking. The system will consist of 7 strings. In the RFQ I quoted the feeder from the panels to the building be a 250 MCM to keep the power losses under 4%.
OK I get one bid back from a contractor that quotes running 15 #6 AWG or one pair of 6 AWG from each string plus 1 ground. I quized him about why and he replies the labor and cable will be less expensive. OK I don't have a problem saving money, but I am not sure running 7 feeders will comply with 690. I cannot find anything that prohibits it, nor do I find anything that allows it either. I just have never seen done this way.