Lb,lr, ll, c condalet

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Nope.

If you look at a standard 2" conduit body it will say 3 - 4/0s max.

Use a section of 4" x 4" NEMA 1 trough instead of a conduit body or increase the size of the conduit body.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Interesting that it is marked on the emt LB's etc, but I have never seen it on a 2" PVC LB. I will have to check more closely. :)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Interesting that it is marked on the emt LB's etc, but I have never seen it on a 2" PVC LB. I will have to check more closely. :)
The only way you can get around the sizing rule in 314.28(A)(2) is if the maximum size and number of conductors is marked on the LB. 314.28(A)(3). This is a rule that is often violated as many assume that the wire fill for a conduit body is the same as the conduit. This is not true for conductors that are #4 and larger.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I actually looked inside the 2" PVC LB at the supply company and it stated 3-4/0 wires. I guess that means I could put 2- 3/0 and 1- 1/0 with #6 ground. This is what I usually do....

3- 4/0 assuming THHN is equal to .9711 sq. in.
2- 3/0, 1- 1/0 and #6 is equal to .7720 sq. in.

Not sure how to convert since insulation size is not mentioned. Perhaps the insulation would not be needed for the calculation. That seems odd- why not just state max size 4/0 wire and then give a cu.in size allowable.
 

SEO

Senior Member
Location
Michigan
Dennis your method may make sense but the stamping states a max of three conductors with a max size of 4/0. There was another thread on this topic that You may want to take a look at. If all your conductors are under #4 than you are not limited to 3 conductors.
 
Last edited:

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
I actually looked inside the 2" PVC LB at the supply company and it stated 3-4/0 wires. I guess that means I could put 2- 3/0 and 1- 1/0 with #6 ground. This is what I usually do....

3- 4/0 assuming THHN is equal to .9711 sq. in.
2- 3/0, 1- 1/0 and #6 is equal to .7720 sq. in.

Not sure how to convert since insulation size is not mentioned. Perhaps the insulation would not be needed for the calculation. That seems odd- why not just state max size 4/0 wire and then give a cu.in size allowable.

Beside the max size, there is also a max number. You can't put 4 4/0 in the aforementioned LB.

There is also bend radius to consider. A single conductor of .940 (900 kcmil) would be tough to install in a 2 inch PVC lb without damage, if not impossible.
 

mcclary's electrical

Senior Member
Location
VA
Beside the max size, there is also a max number. You can't put 4 4/0 in the aforementioned LB.

There is also bend radius to consider. A single conductor of .940 (900 kcmil) would be tough to install in a 2 inch PVC lb without damage, if not impossible.

I vote impossible
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Dennis your method may make sense but the stamping states a max of three conductors with a max size of 4/0. There was another thread on this topic that You may want to take a look at. If all your conductors are under #4 than you are not limited to 3 conductors.

Does it state 3 conductors with a max size 4/0. I didn't have my glasses on so they read it to me. I thought it just stated 3- 4/0 max.

Edit-- I just found an LR in the basement that states vol. 68.4 cu. in. no conductor size....
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't see where the volume enters into this if the conductor size in #4 or larger. There is nothing in 314.28 to even suggest that the volume of the conduit body or of the conductors is part of the sizing of a conduit body or box used as a pull point for conductors #4 and larger. The only thing that enters into the sizing is the size of the raceway.

I have no idea how you can make a calculation for the use of combination of conductors in a conduit body. I see no issue with using the same number of smaller conductors, but when you want to use more conductors than listed on the fitting, I can't see any permission to make any type of calculation.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...

Edit-- I just found an LR in the basement that states vol. 68.4 cu. in. no conductor size....
Then that fitting cannot be used with conductors #4 and larger unless the spacing between the conduit entries meet the requirements in 314.28(A)(2).

You would used the volume to make a calculation as to the permitted number of conductors #6 and smaller based on the conductor volumes found in Table 314.16(B).
 