Anyone familiar with a requirement of a min/max pulling pressure for hospital grade 20A/120V Duplex receptacles and plugs?
A colleague was tasked to gather data on the force required to un-couple the plug and device for a major medical center in Northern New Jersey.
Not sure where this data will be compiled but I'll hunt down the findings! :confused:

Thanks for any help
 

WorkSafe

Senior Member
Location
Moore, OK
Someone may have better info then me, but I might start looking at the UL requirements for these (UL 498, I believe). I'm trying to pull the UL, but not having any luck.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Not sure there is one. but, if you look in a Pass & Seymour catalog, it shows the tests HG receptacles must pass:

They use a 10 lbs abrupt plug removal (10 lbs pulling downward, alternating directions), then the ground pin must not pull out with 4 oz of pulling force.

Then there are some impact tests. See the hospital grade section of the P&S catalog.

Steve
 