Im sizing a breaker for a 20HP elevator motor (208Y-3) I have a chart with the elevator electrical specifications, with the following info:
Rated AC amps: 65.1 amps
Solid State, min-max : 130-293 amps
Motor AC amps: 91 amps
Control Amps: 4 amps
So basically my total amps is 95 amps, would I be OK to put this on say 150A breaker? What scares me is the solid state amps. Any opinions would be helpful, thanks.