Volta
- Columbus, Ohio
I can't give you a clear-cut loophole (yet if it were clear-cut, it wouldn't be a loophole ) because it will be dependent on the particular purpose of the fiber.
If it is for communications as defined by 800 def's, then it would not have to comply with 770, as 800.3(A) excludes any provision in Chapters 1 through 7 unless specifically referenced. So we're back to okay per an Article 800 installation.
If it is not a communications cable, then 770 applies. However, 770.3 Other Articles, second sentence states, "Only those sections of Chapter 2 and Article 300 referenced in this article shall apply to optical fiber cables and raceways." That seems to me to exclude Article 352 permitted and not permitted uses, as the only mention of Article 352 anything is in 770.48 regarding outside and entering buildings. But that is just my opinion and subject to varied interpretations, mostly because 770.110 says Chapter 3 rather than Article 300 :roll:
Well I would need to start into more subtleties than either of us might like at this point, like the definition of a cable in Art. 800, the scope of 800 pertaining to circuits, etc.
I think that 770.6 is clear that the purpose of the fiber is not relevant, and it is not a 725 or 800 method but a 770 method.
770.3 not withstanding, 770.110 (new this cycle, btw) as you have shown, clearly requires the wiring method to comply with Ch. 3, which we might agree was just an easy way of covering whichever method is chosen.
We may further agree that the intent in the NEC in general (I know ) is to prohibit the use of PVC conduit in gathering spaces where more than 100 persons may meet, and we know that any fumes that occur will be toxic regardless of how we classify our installed system.
I think that the PVC would need to be listed as a Riser Fiber Optical Raceway to be used this way in the described building. Best I can do. Or encase it in concrete .