Hello everyone, first time posting here!
(a side note, how do I attach a picture)
I've been having an intermittent ground issues on one of my 480V switch gears lately. What's frustrating is that it comes and goes. When it happens, it actually hits and clears within seconds, and would just repeat for either minutes or hours. So our alarm registry would actually pick up hundreds of the same "ground alarm" within hours. What's more, when it does happen, it's not the common one like we normally see (i.e. one of the three light bulbs not lit anymore,and you turn off load until you see it's lit again) it makes all three lights flicker at the same time, but after the ground goes away, everything would be back to normal.
I've used a FLUKE Power Analyzer to see what's really going on, just to rule out it's not from the instrumentation from my switchgear. The result is: the switchgear, and the alarm is telling me what it is, I have an intermittent ground (i.e. voltage dip) on phase B. When ground happens, phase B would dip, the phase-gnd voltage would go as low as some 130V, and phase A,C phase-gnd voltage would spike up to some 590V, which makes sense for an ungrounded system like we have.
Now the challenge is to find this ground, which is a pain in the butt, especially given the fact that it comes and goes, and there's no pattern and it's been very erratic. However, the real reason I'm posing is simply to ask:
What if we have an intermittent ground on the primary side of my transformer (2400V/480V), would it cause problem on my secondary side the 480V? Vise versa, could a problem on the secondary side 120V cause voltage spike/dip on the primary side of a 480V/120V transformer?
My plant has ungrounded system on 2400V, 480V. (2400/480 are phase-to-phase voltage)
I ask this because transformer is about the only thing that I haven't been able to check.
Any other advice and ideas would be greatly appreciated!
(a side note, how do I attach a picture)
I've been having an intermittent ground issues on one of my 480V switch gears lately. What's frustrating is that it comes and goes. When it happens, it actually hits and clears within seconds, and would just repeat for either minutes or hours. So our alarm registry would actually pick up hundreds of the same "ground alarm" within hours. What's more, when it does happen, it's not the common one like we normally see (i.e. one of the three light bulbs not lit anymore,and you turn off load until you see it's lit again) it makes all three lights flicker at the same time, but after the ground goes away, everything would be back to normal.
I've used a FLUKE Power Analyzer to see what's really going on, just to rule out it's not from the instrumentation from my switchgear. The result is: the switchgear, and the alarm is telling me what it is, I have an intermittent ground (i.e. voltage dip) on phase B. When ground happens, phase B would dip, the phase-gnd voltage would go as low as some 130V, and phase A,C phase-gnd voltage would spike up to some 590V, which makes sense for an ungrounded system like we have.
Now the challenge is to find this ground, which is a pain in the butt, especially given the fact that it comes and goes, and there's no pattern and it's been very erratic. However, the real reason I'm posing is simply to ask:
What if we have an intermittent ground on the primary side of my transformer (2400V/480V), would it cause problem on my secondary side the 480V? Vise versa, could a problem on the secondary side 120V cause voltage spike/dip on the primary side of a 480V/120V transformer?
My plant has ungrounded system on 2400V, 480V. (2400/480 are phase-to-phase voltage)
I ask this because transformer is about the only thing that I haven't been able to check.
Any other advice and ideas would be greatly appreciated!