Is it permissable by code to install in a three phase ( using single core cables) system to install the earth and the neutral conductors in a different conduit of the same duct bank?
Is it permissable by code to install in a three phase ( using single core cables) system to install the earth and the neutral conductors in a different conduit of the same duct bank?
300.5(I) Conductors of the Same Circuit.
All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be installed in the same raceway or cable or shall be installed in close proximity in the same trench.
Exception No. 1: Conductors in parallel in raceways or cables shall be permitted, but each raceway or cable shall contain all conductors of the same circuit including equipment grounding conductors.
Exception No. 2: Isolated phase, polarity, grounded conductor, and equipment grounding and bonding conductor installations shall be permitted in nonmetallic raceways or cables with a nonmetallic covering or nonmagnetic sheath in close proximity where conductors are paralleled as permitted in 310.4, and where the conditions of 300.20(B) are met.
Quite apart from if code allows (which if I've understood your question correctly, it doesn't), if the neutral is in a different metallic conduit from the phase conductors and there is a metallic path between the seperate conduits then there will be an inductive heating effect, which will (at best) cause heating and power loss due to heating, and at worst will melt the insulation of the cores causing failure, and/or possibly fire.a three phase ( using single core cables) system to install the ... neutral conductors in a different conduit