Is remarking white THHN prohibited?

Status
Not open for further replies.

jtinge

Senior Member
Location
Hampton, VA
Occupation
Sr. Elec. Engr
Have an existing 120 v circuit to a fuel pump. Wiring is in raceways with the appropriate seals and explosion proof fittings. Fuel pump to be changed with a new pump at 208 v. Do I interpret NEC 200.7 correctly that the existing white THHN conductor cannot be reidentified as an ungrounded phase conductor so that the existing wiring can be reused at 208 v? Do the provisions allowing reidentification of the white conductor only apply to cables or flexible cords? What are my options if this is the case?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Your only option at this point is to replace the white wire with another color of wire (Not white or green).

Chris
 

macmikeman

Senior Member
Send it to me, I'll trade ya for black. I am always running out of white conductors, and find I have to make another useless side trip to supply house to get some to finnish the job....
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
OK. I'll say what's on the minds of many forum members:

1) Are you getting the work inspected?

2) Is cost a factor (will you lose the job to someone else).

The electricity doesn't know the color of the wire it's flowing through. As long as the white wire is clearly relabeled, is it really an issue?

Are you suggesting he cheats LOL.
I would if not inspected
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
a wierd solution allowing use of the existing conductors

a wierd solution allowing use of the existing conductors

The new pump is single phase 208V.

Add a 1:1 transformer in the circuit feeding the new pump and ground the secondary of that transformer.
 

peter

Senior Member
Location
San Diego
I'm losing faith in the Code day by day. If this were a new instalation, yes, use the proper color. But seeing as how the old white wire is cemented in, then you are faced with removing and replacing the compound as well as replacing the wire. Maybe $50 or $100 bucks to satisfy some stupid technical rule [in this case] versus 5 cents worth of tape.
And, as is pointed out, the electricity doesn't care.
~Peter
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
Many of these loop through to, so I'm assuming that the breaker you are replacing only feeds the one pump. You would also have to rewire the emergency shutoff switch since it is wired for 120v right now.
 

lunalilo

Member
Wait...

So your nto allowed to use white THHN then recode?

And am I right in thinking that you can recode "any other color" to "any other color" as long as it's not originally gray white or green?
 
Status
Not open for further replies.
Top