Has anyone put in a 1200a service from a utility pole? I've put them in on commercial/Industrial buildings but not from a pole.
This job the utility is going to get me 208/120 3PH from a power line 65ft from the service. I'd be running the service wire up the pole to the MCB. It would be 4 runs of 400Kcmil w/ neutral (3" C.)
It would seem I would run down the pole with 4 runs of PVC, (neutral), go underground all the way to the MCB, all with goosenecks at the top: (that's a lot of geese up there.)
I've always had a pad mount XFMR on the outside and a short run with a wireway or underground into the building; not from a pole 65ft away. The building owner is too cheap to pay for the utility to dig in a pad mount XFMR. Any ideas?? thanks in advance.