I'm having a friendly discussion with my local building inspector as to how to resolve this problem:
An apartment complex constructed in to 70s uses the EMT conduit as a path for ground. This is fine inside, but the contractor also ran the EMT out from the foundation, at ground level, and into each unit's AC disconnect. As you can imagine, 40 years later that EMT has rusted away, interrupting the path to ground.
As each unit only used a 20 amp circuit, and the interior circuits are also 20 amps, my proposal was to make a penetration through an interior receptacle box t othe outside, bond a #12 ground wire to the interior box, and pipe with PVC on the exterior to each disconnect and land the ground. The ground would not be in the same conduit as the phase conductors, but it seems to me that it would ultimately end up at the source if there was a ground fault. Am I over-simplifying this? Any thoughts would be appreciated.
An apartment complex constructed in to 70s uses the EMT conduit as a path for ground. This is fine inside, but the contractor also ran the EMT out from the foundation, at ground level, and into each unit's AC disconnect. As you can imagine, 40 years later that EMT has rusted away, interrupting the path to ground.
As each unit only used a 20 amp circuit, and the interior circuits are also 20 amps, my proposal was to make a penetration through an interior receptacle box t othe outside, bond a #12 ground wire to the interior box, and pipe with PVC on the exterior to each disconnect and land the ground. The ground would not be in the same conduit as the phase conductors, but it seems to me that it would ultimately end up at the source if there was a ground fault. Am I over-simplifying this? Any thoughts would be appreciated.