Here is a question about panel boards. 2 panelboards rated as suitable for use as service equipment make up a service for a building. One panelboard has a 200amp main circuit breaker and the other has a 100amp main circuit breaker. The ungrounded service conductors are size 350-kcmil copper. Ungrounded tap conductors to the 200 amp panelboard are size 3/0 awg copper to the 100A panelboard are size 3 awg copper. The grounded circuit conductor is run to each service enclosure. The grounding electrode conductor is run from the neutral in the wireway to the grounding electrode. Grounding electrode conductor taps are run from the grounding bus in the 100a panelboards to the grounding electrode conductor. The min. permitted size grounding electrode conductor tap for the 100A panelboard is?
If going by Table 250.122 it would be 8 awg? Since this is ungrounded this should be going under table 250.122 and not table 250.66? Would this be a big enough guage?
If going by Table 250.122 it would be 8 awg? Since this is ungrounded this should be going under table 250.122 and not table 250.66? Would this be a big enough guage?