My question is how would you extrapolate the trip time curve for a TA35 breaker in the spec sheet here on pg3 for a 50 -60 amp current lasting only 2 - 3 cycles?
http://www.schurter.ch/pdf/english/typ_TA35_Wippe_1Pol.pdf
Here is some background:
I am wanting to use a 3-5 amp thermal breaker to protect a piece if equipment that normally draws less than 1 amp running. Use the 3 amp , 1 pole, for this discussion. ((although I will most likely use the 5A for increased ability to handle the inrush.))
My concern is inrush current. The Switch Mode Power Supply inside of the equipment states a worst case inrush current of 50 -60amps. Unfortunately they do not state a time duration.
** I measured one example unit and only observed a 2-3 cycle worst case inrush duration.
The amplitude was normally less than 10 amps at 120Vac. I am not sure under what conditions they predict 50 -60 amps (unit can be run at 240V so of course it would be higher there) . I want to design around this worst case value to be safe.
NOTE that there are many different specifications given such as::
Overload: min 40 cycles at 6x In.
Conditional short circuit current : 2000A
And the trip time curves.
From these specifications it can be seen that multiple overloads cause degradation of the unit thus limiting its life.
My question is actually two fold:
1) How many cycles do you think this breaker will hold for at 50-60 amps.
2) How much of a concern for the life of the breaker should there be if powering up inrush current is 50 -60 amps lasting for only 2-3 cycles?
http://www.schurter.ch/pdf/english/typ_TA35_Wippe_1Pol.pdf
Here is some background:
I am wanting to use a 3-5 amp thermal breaker to protect a piece if equipment that normally draws less than 1 amp running. Use the 3 amp , 1 pole, for this discussion. ((although I will most likely use the 5A for increased ability to handle the inrush.))
My concern is inrush current. The Switch Mode Power Supply inside of the equipment states a worst case inrush current of 50 -60amps. Unfortunately they do not state a time duration.
** I measured one example unit and only observed a 2-3 cycle worst case inrush duration.
The amplitude was normally less than 10 amps at 120Vac. I am not sure under what conditions they predict 50 -60 amps (unit can be run at 240V so of course it would be higher there) . I want to design around this worst case value to be safe.
NOTE that there are many different specifications given such as::
Overload: min 40 cycles at 6x In.
Conditional short circuit current : 2000A
And the trip time curves.
From these specifications it can be seen that multiple overloads cause degradation of the unit thus limiting its life.
My question is actually two fold:
1) How many cycles do you think this breaker will hold for at 50-60 amps.
2) How much of a concern for the life of the breaker should there be if powering up inrush current is 50 -60 amps lasting for only 2-3 cycles?