Just a couple of questions that resulted from confusion from article 695.
If I have a 100HP fire pump @ 208-3 phase + a 1-1/2 HP jockey pump
Fire Pump FLC = 273A
Jockey Pump FLC = 6.6A
Total @125% = 349.5
Design ampacity = 400.0
Fire Pump LRA = 1603A
Jockey Pump LRA = 44A
Total = 1647A
Design Ampacity = 1800A
So my feeder can be rated at 400amps, and my disconnect (non fused) should be rated @ 1800amp.
Questions:
Should my ground from the disconnect to the fire pump controller be sized per 250.122 (or) 250.66?
Also, if the feeder has to run inside the building what type of wire is required, as I understand it has to be rated for 2 hours.