does the adjustment factor table 310.15(b)(2)(a) apply to incoming service
example 8 250kcmils thwn al
410amp at 70 percent 287amps
does that seem correct
thank as always
 

cripple

Senior Member
service

310.15(B)(2)(a) would apply, but I come up 322 Amps not 287.
When adjusting the allowable ampacity you can use the 90 degree column, which is 230 amps.
Now you would 460 X .70 = 322 amps.
 