An additional building on the same property is supplied with an outside multiwire branch circuit which includes an equipment grounding conductor. This building does not have nor need a grounding electrode. 2005NEC Sec. 250.32.
This outside multiwire branch circuit's disconnecting means is located not on this additional building but on an adjacent building 25 feet away. 2005NECSec.225.32.
An overhead Coaxial Cable (for internet use) is dropped to this additional building and connected on the outside wall to a fitting with a terminal for a wire for bonding/grounding. Another coaxial cable that enters the additional building is also connected to this fitting.
Is it code to run a 6AWG copper wire from this fitting 25 feet underground to the grounding electrode system of the service supplying this additional building? Or must a ground rod be driven at the additional building and bonded to both the fitting and to the grounding electrode system of the service supplying this additional building?
Thanks
This outside multiwire branch circuit's disconnecting means is located not on this additional building but on an adjacent building 25 feet away. 2005NECSec.225.32.
An overhead Coaxial Cable (for internet use) is dropped to this additional building and connected on the outside wall to a fitting with a terminal for a wire for bonding/grounding. Another coaxial cable that enters the additional building is also connected to this fitting.
Is it code to run a 6AWG copper wire from this fitting 25 feet underground to the grounding electrode system of the service supplying this additional building? Or must a ground rod be driven at the additional building and bonded to both the fitting and to the grounding electrode system of the service supplying this additional building?
Thanks