300 mcm how many in conduit per nec code

Status
Not open for further replies.

ohmhead

Senior Member
Location
ORLANDO FLA
Well question for the experts how many 300 mcm xhhw-2 in pvc sch 40 conduit can we install think about it good ? I have another question after any responses.

That compact alu wire also
 

Volta

Senior Member
Location
Columbus, Ohio
PIPE - WIRES
1 --- 1
1.5 - 1
2 --- 3
2.5 - 4
3 --- 7
3.5 - 9
4 --- 12
5 --- 19
6 --- 28

More for nipples. This is for XHHW compact in PVC 40.
 
Last edited:

480sparky

Senior Member
Location
Iowegia
I come up with 5, using Alcan's dimensions. YMMV.

2?" PVC @ 40% fill is 2.181 in?. Dimension given is .3904 in?. 2.181 / 0.3904 = 5.58.

So 5. Final answer. I'm locking it in.
 

480sparky

Senior Member
Location
Iowegia
352.22 Number of Conductors.
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9. C-10 is not mentioned.

Read the beginning of those tables.:
"This annex is not a part of the requirements of this NFPA document but is included for informational purposes only."
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
352.22 Number of Conductors.
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9. C-10 is not mentioned.

Read the beginning of those tables.:
"This annex is not a part of the requirements of this NFPA document but is included for informational purposes only."

So why is it there. I thought that was to save time and not have to calculate but I see that's wrong. Thanks.
 

Volta

Senior Member
Location
Columbus, Ohio
I come up with 5, using Alcan's dimensions. YMMV.

2?" PVC @ 40% fill is 2.181 in?. Dimension given is .3904 in?. 2.181 / 0.3904 = 5.58.

So 5. Final answer. I'm locking it in.
Note 6 of Chapter 9 allows actual dimensions to be used for conductors not included in Chapter 9. However XHHW compact is listed in Table 5A as having an area of .4015 in sq., not .3904.

Also, 2-1/2 schedule 40 available area is not 2.181, you are looking at Type A.
:)
four-- check Table C-10 in Annex C

Occasionally those non-Code tables are wrong, but four is correct here.
 

480sparky

Senior Member
Location
Iowegia
Note 6 of Chapter 9 allows actual dimensions to be used for conductors not included in Chapter 9. However XHHW compact is listed in Table 5A as having an area of .4015 in sq., not .3904.

It's XHHW-2 in the OP, not XHHW. That's why I used a manufacturer's spec.

......Also, 2-1/2 schedule 40 available area is not 2.181, you are looking at Type A..........

So I'm not smarter than a 5th grader. 1.878 / 0.3904 = 4.48.
 
Last edited: