Feeding 15amp branch circuits with 12/2wg

Status
Not open for further replies.

Jim W in Tampa

Senior Member
Location
Tampa Florida
Is it ok to feed 15amp branch circuits with 12/2wg as long as I use 15amp breakers on the circuit

You can use anything that is rated for 15 amps and higher. #12 is fine and often used for the home runs on long runs to help with voltage drop. Problem is you might get an inspector that does not know this. We have had threads before over that issue.
 