I have come upon an installation that I question if it is code compliant.
There is a multiple gang meter enclosure (3),with two(2), 200A services and one (1), 100A service. The source voltage is 120/208, 3PH,4wire. All of the grounding electrodes are bonded at the meter enclosure to a common bus that is bonded to the system grounded conductor. At the service disconnecting means there are three(3) phase conductors and the grounded conductor. Shouldn't there be an equipment bonding jumper from the meter enclosure? The raceway system is PVC.
There is a multiple gang meter enclosure (3),with two(2), 200A services and one (1), 100A service. The source voltage is 120/208, 3PH,4wire. All of the grounding electrodes are bonded at the meter enclosure to a common bus that is bonded to the system grounded conductor. At the service disconnecting means there are three(3) phase conductors and the grounded conductor. Shouldn't there be an equipment bonding jumper from the meter enclosure? The raceway system is PVC.