Entering top of outdoor panel...

Status
Not open for further replies.

davedottcom

Senior Member
Is a hub still required when entering the top of an outdoor panel if a liquid tight connecter is being used?
 

davedottcom

Senior Member
Actually, the one I'm talking about is a 3" Metallic Liquid Tight Male Adapter (with the little rubber washer) entering into the top of an outdoor disconnect.
 

Volta

Senior Member
Location
Columbus, Ohio
If they are listed for use in wet locations, then it is probably acceptable without a hub- 312.2. I would go to great lengths to avoid it, though.
 
Status
Not open for further replies.
Top