Dining Room
A/A Fuel GTX
WI & AZ
I have two SABC's feeding the kitchen recepts. I have another AFCI protected circuit feeding two recepts in the dining room. Can I also feed the living room recepts from the dining room circuit?
cpal
MA
(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
A/A Fuel GTX
WI & AZ
The 2 SABC's are not supplying any other outlets. The dining room is small and there are only two recepts on that circuit. My question is can the dining room circuit feed other outlets? Prior to AFCI requirments, I would feed the DR recepts from the SABC's. FWIW, I use a MWBC to feed my SABC's so AFCI incorporation is not possible.
Read again I believe it says the 2 or more SABC shall not feed any other outlets or something very close to that. The dining room receptacles are required to be on the 2 or more SABC. If you run a separate circuit for the dining room receptacles it is still considered a SABC.
As far as your MWBC it is not possible to use it anymore unless you can get a 2 pole AFCI breaker.
Split Bolt
AFCI protection on your MWBCs is possible. You'll need to use a 2-pole GFCI breaker. As far as feeding off of you dining room receptacles for something else, it doesn't matter how small the dining room is. The code requires 2 or more SABCs. You installed more than the minimum 2, but they are still SABCs and cannot feed other circuits.
Buck Parrish
NC & IN
Here is a shared neutral 2 pole afci http://www.arcadvisor.com/afci.html
A/A Fuel GTX
WI & AZ
Ok, I got it. The dining room circuit is considered a SABC. I knew it could be fed from a SABC but assumed it could also be independent from the SABC if desired.
Jim W in Tampa
Tampa Florida
You do not need to have 2 circuits in the dining room. However you still can not feed other areas like living room off of it. Dining room is a SA circuit and no lights off it either
charlie b
Lockport, IL
Retired Electrical Engineer
210.52(B) has a list of the rooms that are required to be served by the SABC's. Living Room is not on that list. That is the essence of the issue.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
The dining room recep. do not need to connect to the SABC in the kitchen however they are considered to be a sabc. I usually run a separate circuit for the dining room since those recep. must be on AFCI. Then I have 2 or more SABC's for the kitchen.
A/A Fuel GTX
WI & AZ
Yep......That's how I did it but it sure was nice pre AFCI days when you could just tap off one of the SABC's for the dining room, which brings me to another question. Is the "Dining Room" the NEC refers to a formal dining room or is it like so many of my jobs, where you have a kitchen area with maybe a peninsula acting like a dividing line where the table and an overhead fixture are on the other side? I don't see dining room in Article 100.
electricmanscott
Boston, MA
You can still jump off a SABC to feed the DR.
I don't think there is a yes or no to your question that covers all instances.
Dennis Alwon
Chapel Hill, NC
I agree with Scott but the dining area is usually a pretty defined space. It includes formal dining rooms as well as breakfast nooks, IMO.
A/A Fuel GTX
WI & AZ
So basically, it's common sense and AHJ reasoning. Lets see, is it a living room with a table and chairs in it or is it a dining room with a fireplace and big screen TV? I would think anything less than a formal dining room would be out of the realm of enforcement.
Dennis Alwon
Chapel Hill, NC
So we're back to 'what the room is labeled on the print' argument again?
Well, if the plan has a room labeled as a breakfast nook then I think the inspector has every right to enforce that as such.
We had a job in the next city where we had a huge walk in closet. I mean 30' x 20' or so. Cabinets with doors all around the perimeter and a table in the center. They wanted a chandelier there. The inspector said get the plan changed and call it a dressing room and he had no problem with it since all the clothing was inside cabinets. As long as the plans stated closet then the chandelier would be a violation in there eyes.
A/A Fuel GTX
WI & AZ
And you would be wrong. Trust me, esp. if there are plans are marked breakfast nook or something like that, you will need to be on a SABC.
Plans??? Around here, everything is design build meaning I get a set of 8X10 drawings from the lumber yard that only show the door swings and overall dimensions of the rooms. Then I wire at will..........