A question on a practice test is The 15,20,60A branch circuits running in the same raceway. How many grounding conductors shall be installed for these circuits?
thank you, I will read it all that is the way I prefer to learn
Are you planning to take credit for the conduit, despite the question not telling us what material is used for the conduit?my answer is zero.
A question on a practice test is The 15,20,60A branch circuits running in the same raceway. How many grounding conductors shall be installed for these circuits?
huh? is the green stuff supposed to be the egc?
One.
And it'd be a #10
How do you know that?
My guess is that a #10 is too small.
Why would a #10 be too small?
Why would a #10 be too small?
I have the same question. T250.122 says #10 for 60 amps. What am I missing?:-?
Are you planning to take credit for the conduit, despite the question not telling us what material is used for the conduit?