Currently have 2x 15A, 230V circuits running from main service panel to pool equipment (6 wires total). Existing buried conduit is 1/2 in PVC (90C).
I want to install a sub panel for a fancy new equipment controller and would like to replace the 15A circuits with a single 50A feeder to the sub for distribution to the equipment, lighting, backyard outlets etc.
First questions are on the capacity of 1/2 in conduit:
Have found little information on combined wire gauges in conduit but if i calculate the areas, 3x 8 AWG and 1x 12 AWG conductors (THWN insulated) are below 40% of the internal area of Sch 40 rigid PVC conduit. Am wrong and/or in violation of code to run this?
If I run a bare #12 ground conductor I get a little more room and probably ease in pulling. Is this okay in buried rigid NM conduit?
Second questions are regarding whether i need the 4th wire at all:
If the sub panel gets bonded to the pool ufer ground, and there is no conductive path between the pool, equipment or sub panel and the house other than the feeder conductors, am I in violation if I bond the neutral bar to the ground in the sub panel?
I'm relatively certain i know the answer or at least that regardless of the answer, the best practice would be to keep the lowest resistance ground fault path through the ground to the main but couldn't the ufer ground of the pool structure be lower resistance anyway?
I've found a lot of discussion about bonding/grounding of sub panels but little specifically relating to pool equipment subs so I thought I'd throw this in here.
I appreciate any feedback.
I want to install a sub panel for a fancy new equipment controller and would like to replace the 15A circuits with a single 50A feeder to the sub for distribution to the equipment, lighting, backyard outlets etc.
First questions are on the capacity of 1/2 in conduit:
Have found little information on combined wire gauges in conduit but if i calculate the areas, 3x 8 AWG and 1x 12 AWG conductors (THWN insulated) are below 40% of the internal area of Sch 40 rigid PVC conduit. Am wrong and/or in violation of code to run this?
If I run a bare #12 ground conductor I get a little more room and probably ease in pulling. Is this okay in buried rigid NM conduit?
Second questions are regarding whether i need the 4th wire at all:
If the sub panel gets bonded to the pool ufer ground, and there is no conductive path between the pool, equipment or sub panel and the house other than the feeder conductors, am I in violation if I bond the neutral bar to the ground in the sub panel?
I'm relatively certain i know the answer or at least that regardless of the answer, the best practice would be to keep the lowest resistance ground fault path through the ground to the main but couldn't the ufer ground of the pool structure be lower resistance anyway?
I've found a lot of discussion about bonding/grounding of sub panels but little specifically relating to pool equipment subs so I thought I'd throw this in here.
I appreciate any feedback.