The amperage rating of the breaker is not really relevant when a circuit is shorted to ground.
A 20 amp breaker will not trip once it reaches 20.00000001 amps. Nor will a 100 amp breaker open as soon as the current reaches 100.00000001 amps.
In a short circuit, the full load current available to the circuit will flow, and it only takes one or two cycles for it to reach that point. Depending on the transformer, resistance in the circuit, and other factors, it may be 5,000 amps and up.
The ground wire only needs to be capable of carrying that 5k+ amps until the OCPD opens. With a fuse, that's only 3-5 cycles. But a circuit breaker usually needs 5-15 cycles to reacte. So #18 and 16 won't do it. So 15a circuits need 14 ground, 20a needs 12, etc. Once you get to 40- and 50- amp circuits, the current flow will be higher due to the lower resistance of the larger ungrounded circuits. But in those cases, a #8 will still carry enough current long enough to operate the OCPD.
Get into larger circuits, like 100 amps and up, the ratio between the ungrounded and grounded is maintained.