The requirements for protecting the branch-circuit conductors, control apparatus, and circuits supplying hermetic refrigerant motor-compressors against short circuits and ground faults are in [440.22].[/FONT]
[FONT=Arial, Helvetica, sans-serif]
The size and type of the short-circuit and ground-fault protection device for air-conditioning and refrigeration equipment are often marked on the equipment nameplate. The manufacturer calculates these ratings per [440.22] and [440.32] (Figure 440-5).[/FONT]
[FONT=Arial, Helvetica, sans-serif]
If the equipment nameplate specifies "Maximum Fuse Size," use a one-time or dual-element fuse. If the nameplate specifies "HACR Circuit Breaker," use an HACR-rated circuit breaker [110.3(B)][/FONT]
[FONT=Arial, Helvetica, sans-serif]
.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Short-circuit and ground-fault protection cannot exceed the nameplate ratings. If the equipment does not have a nameplate specifying the size and type of protection device, how do you size those devices? That depends on whether you are sizing for multiple motors or a single motor.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Rating for Equipment. Where the equipment incorporates more than one hermetic refrigerant motor-compressor, or a hermetic refrigerant motor-compressor and other motors or other loads, size the equipment short-circuit and ground-fault protection with the "largest load" method. The rating of the branch-circuit short-circuit and ground-fault protective device cannot exceed the largest motor-compressor short-circuit ground-fault protection device plus the sum of the rated-load currents of the other compressors.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Size the branch-circuit conductors at 125 percent of the larger motor-compressor current plus the sum of the rated-load currents of the other compressors [440.33].[/FONT]
[FONT=Arial, Helvetica, sans-serif]
One Motor-Compressor. The short-circuit and ground-fault protection device for motor-compressor conductors must be capable of carrying the starting current of the motor. Also, the protection device cannot exceed 175 percent of the equipment load current rating.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
If the protection device sized at 175 percent is not capable of carrying the starting current of the motor-compressor, you can use the next larger protection device if it does not exceed 225 percent of the motor-compressor current rating.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Test your knowledge with this question: [/FONT]
[FONT=Arial, Helvetica, sans-serif][/FONT]
[FONT=Arial, Helvetica, sans-serif]
What size conductor and protection must you have for a 24A motor-compressor on a 240V circuit (Figure 440-6)?[/FONT]
- [FONT=Arial, Helvetica, sans-serif]10 AWG, 40A[/FONT]
- [FONT=Arial, Helvetica, sans-serif]10 AWG, 60A[/FONT]
- [FONT=Arial, Helvetica, sans-serif]A or B[/FONT]
- [FONT=Arial, Helvetica, sans-serif]none of these[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Answer: (a) 10 AWG, 40A protection.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Here's how we arrive at that answer:[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Step 1: Size the branch-circuit conductor [Table 310.16 and 440.32].[/FONT]
[FONT=Arial, Helvetica, sans-serif]
24A x 1.25 = 30A, 10 AWG, rated 30A at 60?C [110.14(C) and Table 310.16].[/FONT]
[FONT=Arial, Helvetica, sans-serif]
Step 2: Size the branch-circuit protection [240.6(A) and 440.22(A)].[/FONT]
[FONT=Arial, Helvetica, sans-serif]
24A x 1.75 = 42A, next size down protection = 40A.[/FONT]
[FONT=Arial, Helvetica, sans-serif]
If a 40A protection device is not capable of carrying the starting current, you can size the protection device up to 225 percent of the equipment load current rating (24A x 2.25 = 54A, next size down 50A).