Red Wiggler

Senior Member
I have a job where the engineer is requesting "in-line" din rail mounted 120 volt TVSS units for each control circuit (line side) in all control panels we provide. He also wants a TVSS unit on the load side of the control circuit as well.

My question is involves where in the line side control power feed should I mount a TVSS. Can it be ahead of the "Stop" button, or should it be right after the "Stop" button? Or would it even matter?

I guess that he is worried about line surges coming from either side of the Control Panel whether it is line side or load side.

Has anyone ever seen this before?
 

tom baker

First Chief Moderator
Staff member
I am working a design for a motor controller with PLC and have spec'd a Sola STV in line 120 V TVSS. Power comes from the control transformer and thru the STV to the controls.

Also before I have used quite a few of Levitons in line TVSS, its a nice unit, but bigger than the sola. From what I recall the inline TVSS have better protection than one fed from a branch circuit.
 