What is an acceptable current unballance on a three phase compressor? I have a fuse that keeps on blowing but when I replace the fuse and put a clamp meter on it it reads fine. One phase though is about 5 amps more than the others.
Acceptable unbalance is 5% for motors.
Details below.
Are you running this off of a true 3 phase service or an idler RPC? Current unbalance is greater if you're using an idler because of the way it works.
If it's running off of a 3ph utility, one technique used is to rotate the wiring
If it's wired:
_A_
B.C
Try
_B_
C.A
Then
_C_
A.B
Use the configuration that yields the least current unbalance
Measure current at all three legs and write them all down, then take the average.
say 24, 27, 29
(24+27+29)/3 = 26.7
26.7 = mean
Find the one that's furthest from average, so
26.7-24 = 2.7
or...
24-26.7 = |2.7|
Take the difference over the mean (if the highest deviation is higher than average, then use the absolute value)
2.7/26.7 =0.101 = 10.1% current inbalance.
If you tried all three configurations and can't make it be below 5%, you need to address it upstream.