I don't understand. If the trany is indoors in an area that does not require GFCI then you would not need GFCI protect. The GFCI will not help on the secondary side of the trany.I would also supply the Xfrmr with a GFCI receptacle if its serving the exterior. Check with the wording for exterior circuits & receptacles etc.
If you put the transformer inside then the low voltage cable would have to be changed to a chapter 3 method or one that would be legal inside a building. As far as I know the UG cable does not have a verticle flame rating and thus cannot be used indoors.
Sure you can run cable in conduit. People do it all the time even seen nm cable in conduit. As long as the conduit is sized properly there is no problem.So UG cable has to be conduit if it's ran indoors? I thought you can't run cable in conduit?
Sure you can run cable in conduit. People do it all the time even seen nm cable in conduit. As long as the conduit is sized properly there is no problem.
I don't believe you can even sleeve the LV cable in conduit and be compliant.
So under no circumstances can the LV cable be installed indoors? What is the
technical name for this cable? Like romex is really NM-B cable.
I thought you can't put a raceway in a raceway? Is cable considered a raceway?
Sure you can run cable in conduit. People do it all the time even seen nm cable in conduit. As long as the conduit is sized properly there is no problem.
I don't believe you can even sleeve the LV cable in conduit and be compliant.
Sure you can run cable in conduit. People do it all the time even seen nm cable in conduit. As long as the conduit is sized properly there is no problem.
I don't believe you can even sleeve the LV cable in conduit and be compliant.