220 volt pool pump

Status
Not open for further replies.

bccodes

Member
Location
Altoona Pa
I am dealing with an installation of an in-ground pool where the pump is 220volt. Will a double pole gfi breaker work on a 220 volt pump motor that has no nuetral.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Actually, 430.52 is what allows it. Please explain.
430.52 limits your SCGF potection to 250% od FLC in most cases.
To esceed 20 amps, your pump would need to be larger than 2 HP.
Most of the pool pumps I have seen are not.
 

lakee911

Senior Member
Location
Columbus, OH
:D:D
The GFCI portion of the CB won't work without the neutral pigtail connected to the neutral bus.

If neutral of a GFCI circuit breaker is not connected, it will only function as a circuit breaker.

Oh ok .. maybe we should put a switch on the wire? We can label the ON as "Safe" and the OFF as "Prevent nuisance trip at 3:00A Sunday holiday in the snow, dark, on vacation, uphill with no shoes." Oh wait, that probably won't fit ...:D
 