When installing a new panel on an existing home, does the 210.12 B apply to the wires and circuits that are not being replaced or upgraded?
except of course the bedrooms per 2006 NEC.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
When installing a new panel on an existing home, does the 210.12 B apply to the wires and circuits that are not being replaced or upgraded?
except of course the bedrooms per 2006 NEC.

Around here you are not required to afci a circuit if all you do is change the panel out. If you add to the circuit then you must AFCI the circuit. I would check with the AHJ because some areas req. you to use AFCI on a changeout.
 