should the OP follows after derating the current carrying conductors? I have a scenario here where i use a bunch of 20A CB"s for landscape lightings. We pulled 20-#12AwG THHN-THWN-2, 90deg. via 1-1/4" RNC going to the lighting panelboard. Since art. 310.15(B)(2)(a) requires 50% derating and the ampacity of no.12 is 30A, do i need to change the OP to 15A? or upsize cable to No.10 which has an ampacity of 40A? or am i interpreting it incorrectly?