IllinoisElectrician
Member
If you have multiple electric baseboard heaters (say 20) in a house, and you keep each circuit at 30A and you have a couple 30A breakers, are you required to have 1 common disconnect to open all of thes circuit at once?
424.19 seems to indicate that you would need all of those circuits in their own sub panel and have a disconnect on the supply side. It says that "Where heating equipment is supplied by more than one source, the disconnecting means shall be grouped and marked." Maybe that is an alternative to having a single disconnect to kill all the circuits?
However, 424.19(C)(3) says that in a single family dwelling, the service disconnect counts.
Does this mean I can just put a couple 30A breakers in the main panel and call it a day?
424.19 seems to indicate that you would need all of those circuits in their own sub panel and have a disconnect on the supply side. It says that "Where heating equipment is supplied by more than one source, the disconnecting means shall be grouped and marked." Maybe that is an alternative to having a single disconnect to kill all the circuits?
However, 424.19(C)(3) says that in a single family dwelling, the service disconnect counts.
Does this mean I can just put a couple 30A breakers in the main panel and call it a day?