Looking at a Jefferson single phase transformer with 120/240 secondary windings,,,,,,,,,,,,,,the connection diagram states for 120V service to interconnect X1 to X3 and X2 to X4 then secondary connection for 120V is X1 - X4.

Now the question is why put the two secondary windings in parrallel,why not just leave it alone and connect the needed secondary lines to either X1- X2 or X3 - X4?

The only reason I can see is that if not connected in parrallel,then you would still have the possibility of 240V across X1-X4 when you didn't want it if X2 - X3 somehow got shorted.

What do the experts say?

dick
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I believe if you only connected to X1-X2 for the 120V, you'd only be getting half of the transformer's rated VA. By paralleling the secondary windings you get the full rating at 120V.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I wonder if the code would allow the secondary windings to be protected separately? For example, on a 10kVA, 480-240/120V transformer, could you protect it with a 50A c/b on the primary, and two 60A c/b's on the secondary, one for each winding?
 