What year/code cycle did 4 wires for stoves start?

Status
Not open for further replies.

SEO

Senior Member
Location
Michigan
The 1996 NEC section 250-60 was when the change was made .Mobile homes ranges and dryers were required to be four wire prior to the 1996 NEC.
 

hurk27

Senior Member
The 1996 NEC section 250-60 was when the change was made .Mobile homes ranges and dryers were required to be four wire prior to the 1996 NEC.

for manufactured homes, Hud CFR 24 3280.800 which referenced the 1993 NEC required it in 1994:

CFR 24 3280.809 (2) Connection of ranges and clothes dryers with 120/240 volt, 3-
wire ratings shall be made with 4 conductor cord and 3 pole, 4-wire
grounding type plugs,
or by type AC metal clad conductors enclosed in
flexible metal conduit. For 120 volt rated devices a 3-conductor cord
and a 2-pole, 3-wire grounding type plug shall be permitted.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Maybe the real question is when did it become an issue that you could not use a 3 wire connection from a sub panel.

The answer is I think never
 