I'm trying to sort out if NM is allowed to be exposed within a kitchen cabinet between the drywall (if the back of the cabinet is open) or the cabinet back or bottom and a surface-mount box mounted inside the cabinet.
Do you wire these using MC cable, or bare NM? Do you put the NM straight into the surface-mounted box, or through the cabinet first? (If you go straight into the box, how do you handle clamping requirements?) Some electricians I've worked with use a bit of flexible conduit between the box and the wall, or the box and the hole in the cabinet back or base.
I can't find anything in the NEC that makes me think that bare NM is not allowable. 334.12.A says that "exposed and concealed work in normally dry locations" is allowable; and any kitchen cabinet is such a location, isn't it?
Is the interior of a kitchen cabinet an exposed area that makes "protection from physical damage", per 334.15.A, a requirement?
Reading through 300.4, I don't see anything that pertains to non-enclosed areas, except for 300.4.C, which is about "spaces behind panels designed to allow access" -- which is exactly what a kitchen cabinet is, is it not?
There are days when I feel like I totally understand the code, and there days when I fell baffled.
Do you wire these using MC cable, or bare NM? Do you put the NM straight into the surface-mounted box, or through the cabinet first? (If you go straight into the box, how do you handle clamping requirements?) Some electricians I've worked with use a bit of flexible conduit between the box and the wall, or the box and the hole in the cabinet back or base.
I can't find anything in the NEC that makes me think that bare NM is not allowable. 334.12.A says that "exposed and concealed work in normally dry locations" is allowable; and any kitchen cabinet is such a location, isn't it?
Is the interior of a kitchen cabinet an exposed area that makes "protection from physical damage", per 334.15.A, a requirement?
Reading through 300.4, I don't see anything that pertains to non-enclosed areas, except for 300.4.C, which is about "spaces behind panels designed to allow access" -- which is exactly what a kitchen cabinet is, is it not?
There are days when I feel like I totally understand the code, and there days when I fell baffled.