I installed 2 pvc conduit runs under the building slab to an interior mechanical room, these runs are unfused ( straight out of exterior c.t. cabinet ) . I will have about 3ft of conduit exposed to reach bottom of panels, would schedule 80 pvc be an approved means of protection
 

Cavie

Senior Member
Location
SW Florida
I installed 2 pvc conduit runs under the building slab to an interior mechanical room, these runs are unfused ( straight out of exterior c.t. cabinet ) . I will have about 3ft of conduit exposed to reach bottom of panels, would schedule 80 pvc be an approved means of protection

Depends on your AHJ. I have always used Sch 40.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I installed 2 pvc conduit runs under the building slab to an interior mechanical room, these runs are unfused ( straight out of exterior c.t. cabinet ) . I will have about 3ft of conduit exposed to reach bottom of panels, would schedule 80 pvc be an approved means of protection
Absolutely, and I agree with Cavie schedule 40 would be fine in a building, IMO.
 