Is there any provision in the code for running a separate ground wire to the metal boxes of old ungrounded lights?
Hi Chris, I was aware of 250.130C for adding a ground wire for grounding a receptacle but I wasn't sure if it also allowed for adding a ground wire to any ungrounded box because it only makes reference to receptacles. Does 250.130C allow for other applications as well? Thanks, Trent
How does this go non par with NEC 2008 300.3(B)
it doesn't, equipment grounding conductors are not allowed to be run separate except in a very few places, and for very short runs, like 6'
So how does one apply 250.130?? it appears that the ground wire will be run out side of the other conductors since its added later! Sometimes the code is just not as clear in some areas.
How does this go non par with NEC 2008 300.3(B)
it doesn't, equipment grounding conductors are not allowed to be run separate except in a very few places, and for very short runs, like 6'
So how does one apply 250.130?? it appears that the ground wire will be run out side of the other conductors since its added later! Sometimes the code is just not as clear in some areas.
you know, I have no idea, I have never been given a clear reason why the exception to 250.134(B) cant be used other then we know that when a grounding conductor is run seperatly from the circuit conductors it increases the impedance of a circuit in a fault condition, but it does clearly state it can be ran seperatly.
I know I argued this years ago on here, and for the life of me, I cant remember why I was told it wasn't allowed.