EIA-485 to RS232 ?

Status
Not open for further replies.

bwen

Member
Help needed on how to download program from PC (RS232 serial port) to SEL-551 relay.

I have the following.

SEL-551 overcurrent relay with EIA-485 serial port (DB9 Female)
1 - +TX
2 - -TX
3 - N/C
4 - +IRIG-B
5 - SHIELD
6 - -IRIG-B
7 - +RX
8 - -RX
9 - SHIELD

Multilin RS232/485 converter C1450110
RS232 (DB9 Female)
RS485 (2 Wires, "+" and "-")
 

bwen

Member
Thanks, but the website seems inactive

Thanks, but the website seems inactive

Thanks, but the website seems inactive
 

jdsmith

Senior Member
Location
Ohio
Help needed on how to download program from PC (RS232 serial port) to SEL-551 relay.

I have the following.

SEL-551 overcurrent relay with EIA-485 serial port (DB9 Female)
1 - +TX
2 - -TX
3 - N/C
4 - +IRIG-B
5 - SHIELD
6 - -IRIG-B
7 - +RX
8 - -RX
9 - SHIELD

Multilin RS232/485 converter C1450110
RS232 (DB9 Female)
RS485 (2 Wires, "+" and "-")

Here is the note from the SEL online configuration page that tells you how to configure the relay if you order it with only an EIA-485 port

SEL website said:
(3) Warning - EIA-485 is for special applications only. SEL strongly recommends ordering an EIA-232 port. If an EIA-485 port is ordered, SEL strongly recommends cable C671A to allow relay programming and event retrieval. All SEL-551 relays ordered with an EIA-485 port are shipped with a C675 Terminal Adapter to adapt from the on board DB-9 connector to an 8-pin screw terminal.

I would suggest you order the SEL #C671 cable. Incidentally, this is one of the reasons I do not allow any new SEL-500 series relays in the plant - they only have one communication port and I want one port avaialble for local programming and another port to connect to a SCADA system. The only exception is we do use SEL-587Z relays, but they are unique and they have multiple communication ports available.
 