250.52(3)

Status
Not open for further replies.

Buck Parrish

Senior Member
Location
NC & IN
If I use a ufer ground (concrete encased rebar 20ft or more).
Do I need to use grd. rods?
And is #4 cu good for a 400 amp service?

This is residential sfd
 

eprice

Senior Member
Location
Utah
If I use a ufer ground (concrete encased rebar 20ft or more).
Do I need to use grd. rods?
no
And is #4 cu good for a 400 amp service?

This is residential sfd
yes

Note: these are NEC answers. An engineer may spec something in excess of the NEC requirement.

Edit: Actually, I guess there aren't many electrical engineers designing single family dwellings ;)
 
Last edited:

raider1

Senior Member
Staff member
Location
Logan, Utah
If I use a ufer ground (concrete encased rebar 20ft or more).

And is #4 cu good for a 400 amp service?

This is residential sfd

Where the grounding electrode system consists of just a CEE then you need not run anything larger than a #4 to the CEE regardless of the service size. (See 250.66(B))

Chris
 