Is it a code violation to change sizes in the middle of a conduit run (rigid)?
Or is it just a bad practice to do so?
 

jusme123

Senior Member
Location
NY
Occupation
JW
Is it a code violation to change sizes in the middle of a conduit run (rigid)?
Or is it just a bad practice to do so?

No its not against code, in fact, its done quit often if you are referring to less conductors as the conduit run continues
 

iwire

Moderator
Staff member
Location
Massachusetts
The NEC does not prohibit changing sizes in the middle of a run of course that assumes you maintain proper conductor fill for the smaller raceway.
 

session88

Member
Location
USA
So it is ok to reduce a conduit size in the middle of a run at a coupling with an RE bushing, or is a condulet or j-box required when changing sizes?
 