Wire Connector/Splice
1. I want to splice #8cu wire to #12 cu wire in a junction box. What type of connector do I use? Is this in violation of NEC 110.14 (A)?
2. Is there a way to terminate #8 cu wires to a 20A branch circuit breaker in a panelboard?
augie47
Tennessee
1. I want to splice #8cu wire to #12 cu wire in a junction box. What type of connector do I use? Is this in violation of NEC 110.14 (A)??
Cu to Cu ?
There are many listed products available from wire nuts to split bolts, etc.
No violation per se.. if Cu to AL the options are fewer.
most manufacturer (if not all) 20 amp breakers will accept a #8
do you know horsegoer ? :)
resistance
WA
Again Ditto!!
To add: If you are not in violation of section 110.3, then i don't see what the problem is!!