archimedes
Member
I wanted to know if this setup would be a violation of the NEC. I have a 3/4" IMC conduit that 90's into an LB conduit body. The conduit body has a 3/4" IMC nipple that is approximately 4.5" long, and ends in a Myers hub. The hub end of the nipple has then been fastened securely into the side of 12" Cope cabletray via an 1.125" hole in the tray. The conduit is supported securely via the NEC instructions for IMC conduit.
In article 392.6(J) it states, "For raceways terminating at the tray, a listed cable tray clamp or adapter shall be used to securely fasten the raceway to the cable tray system..."
Would a Myer's hub constitute as an adapter? Would this be acceptable for grounding purposes?
In article 392.6(J) it states, "For raceways terminating at the tray, a listed cable tray clamp or adapter shall be used to securely fasten the raceway to the cable tray system..."
Would a Myer's hub constitute as an adapter? Would this be acceptable for grounding purposes?