Transformer

Status
Not open for further replies.

Mt.Shasta

New member
Scenario: 150 KVA Transformer in Hollow space (yes against code) over ruled.
25 foot tap rule is in place. but the Secondary Overcurrent is 12 feet above the ground level. following that another 7 feet down to panel LP R 42 space.
I believe it should be no higer then 6 ft. 7?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I would agree as well.

240.24(A) would be the code section that requires the overcurrent protective device operating handle to be not higher than 6'7" AFF.

Chris
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
If the disconnect is at the same level as the transformer, then a distance above 6'7" might be acceptable.
 