Ahhh!!! Now I see what the series question affects!
So what I would have are multiple sets of conductors with 10.5Adc, 566V on each of them going to the combiner(s) that are inside the inverter, right? So I have 15 sets of 2#12 (CU) + 1#12ground in a 1/2" conduit, all going to the inverter's combiner(s) because I have 15 strings. Am I catching a clue now?
Are you sure that the string combiners are "in" the inverter? Or are the combiner boxes separate and combine several "strings" (each fused) into one output (V=string V and A = #strings X panel Amps (plus agj)) that is then sent to the inverter? You would have a different wire size here. There can also be multiple combiners sent to one inverter (if it has a multi-lugged bus) as long as that combination does not exceed the inverters ratings. Also there is line loss on the DC feed to account for from the combiner to the inverter if they are not near by.