lmchenry

Senior Member
I have a 120/208 service with 13 circuits in a 2000 amp MDP. One of the equipment grounds with the feeders has 4 amps on it. Is this uncommon and where would it come from?
 

lmchenry

Senior Member
Maybe better asked would be if in a properly installed service should there be any current on the equipment ground? Could this come from the field around the phase conductors?
 

brian john

Senior Member
Location
Leesburg, VA
Prior to a shut down a full visual inspection and taking voltage readings neutral to ground (with full load) and zero sequence measurements can help isolate the issue.
 