Reviewing a design in progress. Can multiple transformers be fed from a single circuit breaker using a single feeder?:confused:

i.e. Two 5KVA single phase XFMRs (480-120/240V) both fed via a single 2P-30Amp C.B. Single primary feeder taps the primary lugs of XFMR 1 and continues to tap primary lugs of XFMr 2. Anything wrong in th scenario above? If so, I'd appreciate the NEC reference.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Short answer is "yes". As long as you comply with the values in 450.3(B).
In this case you would need to assure the secondary OCP does not exceed 125% of the transformer current.

Some may disagree with my next comment. In your case, 250% of the primary current is 26 amps. My read on 450.3(B) is that there is no provision for "next larger size" when applying the 250% rule, so I feel your primary OCP would need to be 25 amps, not 30.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Found the answer in NEC 450.7. Thanks,

450.7 is for parallel transformers, which would also have the secondaries tied together. It doesn't sound like this is what you have.

Anyhow, I completely agree with Augie and don't see any problem with a single feeder.
 