Cost of using lights
GG
Ft.Worth, T.X.
I come up with $12.60.
Thanks brother. You mind showing me the math, as I have an owner that has a tenant that wants to know how much the light bill is every month. Its an apartment complex and they stuck the 2 outside lights on the tenants panel. There is no house panel.
dbuckley
2 x 175W lamps is a load of 350W
Each hour you consume (350/1000) = 0.35KWh
You operate for 300 hours, so (300 hours * 0.35KWh) = 105KWh
You said ".12 cents a KW hour"; I bet you mean $0.12 or 12 cents per KWh.
So, A KWh costs $0.12, ($0.12 * 105 KWh) = $12.60
Ooh - I agree 480Sparky's numbers - thats cool!
And he beat me to it; must type faster :)
GG
Ft.Worth, T.X.
I was not adding the lights, only replaced a broken photo cell on one of the 2 lights. The apartments are maybe 10 years old, max. How far back does 210.25 go?
cowboyjwc
Simi Valley, CA
If the building is 10 years old, I just looked in the 1996 NEC (just happened to have it handy) and 210.25 is there.
480sparky
Iowegia
Who says they had adopted the '96 at the time? Maybe they were still on the '93, or the '90, or even the '87. Heck, there's no law that says you even have to adopt the NEC. It could have been some other standard, even a home-grown one.