Set up as:
440v 3p 60amp breaker to- Delta / Delta transformer to one 220v 3p machine. Code indicates with this I can use the primary OCPD to protect the whole run. Can the whole circuit be wired with a #10 equipment ground? The only breaker ahead of the system is a 60? seems odd to wire for 120 amps and have #10 qualify.
Also a second system is set up the same way except I was handed a Delta / Wye transformer. I disconnected the XO, so there is no neutral or bond. Then I grounded the case, same way as the other. I fear the inspector will nick me on it because code only quotes a Delta / Delta can be done this way only. If he doesnt catch it do any of you see a safety hazard to this?
440v 3p 60amp breaker to- Delta / Delta transformer to one 220v 3p machine. Code indicates with this I can use the primary OCPD to protect the whole run. Can the whole circuit be wired with a #10 equipment ground? The only breaker ahead of the system is a 60? seems odd to wire for 120 amps and have #10 qualify.
Also a second system is set up the same way except I was handed a Delta / Wye transformer. I disconnected the XO, so there is no neutral or bond. Then I grounded the case, same way as the other. I fear the inspector will nick me on it because code only quotes a Delta / Delta can be done this way only. If he doesnt catch it do any of you see a safety hazard to this?