krneison
- Portland, OR
Our AHJ has recently decided that the wiring method that has been practiced for years in G.E. breaker enclosures, model no # SF250S, in the industrial plant we work in is no longer accepted:-? The conductor size is 3/0.
My biggest dilemma is how to interpret the measuring distance from lug to wall. I have attached a picture of the disconnect to this post to see exactly what I am referring to. We have the line coming in from the side bottom and the load coming in from the top of the disconnect. 312.6 (A) (1), I think would apply to this type of installation. The measurement, according to the note under the table says that "the bending space at terminals shall be measured in a straight line from the end of the lug or wire connector (in the direction that the wire leaves the terminal) to the wall barrier, or obstruction." I would think as per table 312.6(A), under one wire per terminal, you would need 4" from the end of the lug to the top of the enclosure. However, the AHJ is calling the 4" from the side of the enclosure to the A phase lug, therefore putting us in violation on the A phases of the Line and load. Now we have to attach 4x4 wireway to each side of the enclosure to account for the bending radius.